Just installed a 240v 18k BTU ductless mini split on my detached garage. I have power to the AC disconnect box, but on the load wires leaving the disconnect box there’s no power. The disconnect switch is installed in the ON position, I’ve triple checked that. According to the manual, the mini split is 20amps, the disconnect I installed is 30amp(recommended by Home Depot), and the breaker for the 240v circuit in my breaker box has a double post 20amp breaker for 40amp total. Any ideas why I’m not getting power to the load wires after the AC disconnect? Sorry if this is a stupid question, but I’m a bit lost right now. Could the disconnect box be bad? Thanks for any help.
It says it’s a fused disconnect, but I didn’t see any fuses?
The Shop
DeCal Works Huge Plastic Inventory of UFO and Polisport kits.
Luxon 4-Post Bar Mounts
$189.95 - $239.95
Both the black and white coming in the back of the disconnect box have power, the black and red running out the bottom of the disconnect box have no power.
If so, that is the fuse able link, I think.
If it comes out, check it across the blades for continuity.
It also may be directional. So it only works one way.
When you pull it, you should see 2 blades on each side.
Those make the circuit. You should have continuity between the two.
Not from each side, but individually.
It makes contact from black to black, and the red to white.
That make any sense?
With the fuse pulled, you should have power where the blades plug in.
If not, something is wrong with the disconnect.
With the fuse pulled, you should have power where the blades plug in.
If not, something is wrong with the disconnect.
The prongs are offset from each other for some reason.
Also leave the fuse out, and check for power where the fuse plugs in.
So I guess I need to get some fuses, apparently they aren’t included. Any suggestion in which type? Says H, K1, K5, K9, etc.
I think you found the problem.
Good luck!
Pit Row
You might consult the A/C manufacturer.
I would guess a fast acting one, that would provide the most protection.
Post a reply to: Electrical and/or HVAC question